OK now. I looked at the schematics - not real hard - and went back and read some of that which you wrote. I think that you have a deeper problem....
First you need to verify that you have proper house wiring with a protective ground. Get an indicator tool or put a GFI where you plug this beast in. (GFI is a great idea)
Typically, our houses (USA) are supplied with 3 wire power. 2 phases and a neutral. Connect the phases and you have 240 volts. Any phase to neutral and you have 120 volts. Having 2 phases is (one of the reasons) why we want to power our audio gear from a single outlet. If we power form 2 outlets that are on different phases we can end up with 240 volts between them. (rare but accidents do happen)
The neutarl line in the interesting thing. In theory it goes all the way back to the generator and forms a return for the current. In practice it goes to the neutral of the nearest power transformer. It should be grounded there and also at your breaker box where it enters your house. The neutral and the protective (green) ground are tied together there and should have a real earth ground (stake, cold water pipe etc) .
The three wires to your ampex should be Hot (black), neutral (white) and ground (green). The hot is at 120 volts and carries current to the Ampex. THe neutral (in theory) should be at ground and carries the current back to the generating plant. And the protective ground should be at the potential of the ground under your feet.
How far away from your ampex is the breaker box? If it is far then the ground under your feet (and the puddle of water you are standing in) could be at a different potential than the neutral wire (death awaits) or protective ground.
Put in a GFI and test your outlet. Be sure that the neutral and ground are tied together and have 0 voltage between them at the outlet.
Sorry for rambling on here.
Neutral is not ground. Take for example the case of a broken neutral wire. Power comes in throuught the hot wire, goes through the fuse/breaker and switch and to a motor. The other wire of the motor is connected to neutral and travels through you ampex to the neutral bus and is broken at one of the connectors (bad connector for example) The neutral wire from the motor to the break is at hot potential. You touch it and you die.
No part of the transport plate should be at any voltage above the protective ground. (not the neutral) This is to keep you from completing a circuit from the puddle on the floor to the transport plate. The plate and other metal parts should be grounded. This is an important test.
It may be that the plate is at protective ground and you have an elevated neutral.
OK, I've blabbed too much....
OH, one more thing. If you have a voltage you want to test you can wire a 120 volt lamp (lightbulb) in series with your meter set on AC current. a 60 watt bulb will pass a max of 0.5 amp at 120 volts so set your meter to the 1 amp scale if it has it. (120 volts / 60 watts = 0.5 amps). This will tell you if the voltages you measure have any power behind them without blowing anything up. Of course if the bulb glows then you know. Even a few mA is too much for me.
--Ethan
First you need to verify that you have proper house wiring with a protective ground. Get an indicator tool or put a GFI where you plug this beast in. (GFI is a great idea)
Typically, our houses (USA) are supplied with 3 wire power. 2 phases and a neutral. Connect the phases and you have 240 volts. Any phase to neutral and you have 120 volts. Having 2 phases is (one of the reasons) why we want to power our audio gear from a single outlet. If we power form 2 outlets that are on different phases we can end up with 240 volts between them. (rare but accidents do happen)
The neutarl line in the interesting thing. In theory it goes all the way back to the generator and forms a return for the current. In practice it goes to the neutral of the nearest power transformer. It should be grounded there and also at your breaker box where it enters your house. The neutral and the protective (green) ground are tied together there and should have a real earth ground (stake, cold water pipe etc) .
The three wires to your ampex should be Hot (black), neutral (white) and ground (green). The hot is at 120 volts and carries current to the Ampex. THe neutral (in theory) should be at ground and carries the current back to the generating plant. And the protective ground should be at the potential of the ground under your feet.
How far away from your ampex is the breaker box? If it is far then the ground under your feet (and the puddle of water you are standing in) could be at a different potential than the neutral wire (death awaits) or protective ground.
Put in a GFI and test your outlet. Be sure that the neutral and ground are tied together and have 0 voltage between them at the outlet.
Sorry for rambling on here.
Neutral is not ground. Take for example the case of a broken neutral wire. Power comes in throuught the hot wire, goes through the fuse/breaker and switch and to a motor. The other wire of the motor is connected to neutral and travels through you ampex to the neutral bus and is broken at one of the connectors (bad connector for example) The neutral wire from the motor to the break is at hot potential. You touch it and you die.
No part of the transport plate should be at any voltage above the protective ground. (not the neutral) This is to keep you from completing a circuit from the puddle on the floor to the transport plate. The plate and other metal parts should be grounded. This is an important test.
It may be that the plate is at protective ground and you have an elevated neutral.
OK, I've blabbed too much....
OH, one more thing. If you have a voltage you want to test you can wire a 120 volt lamp (lightbulb) in series with your meter set on AC current. a 60 watt bulb will pass a max of 0.5 amp at 120 volts so set your meter to the 1 amp scale if it has it. (120 volts / 60 watts = 0.5 amps). This will tell you if the voltages you measure have any power behind them without blowing anything up. Of course if the bulb glows then you know. Even a few mA is too much for me.
--Ethan