Hello again - Velvet Elvis
Sorry if some of this stuff I state here is already familiar to you...
You mentioned:
"I'm not required to have a licensed electrical contractor... only that I pass the city's electrical code test"
This is very common in a lot of municipalities outside of Philly.
My Mom lived in North Jersey, and although I'm BOCA certified as an Electrical Inspector, I didn't need to hire a Licensed Electrical Contractor to install a new service for her house. However I needed to have it inspected by the township Electrical Inspector. He and I were members of the same organization.
As mentioned: 16a x 120v= 1920watts OR 1920 watts / 120 = 16 amps
Hair Dryers are considered to be on only for a short while,
so it wouldn't be necessary to install a dedicated circuit
or ONE single receptacle just for the hair dryer.
Although since 1996, the NEC DOES state that all
NEW bathrooms shall have a GFCI dedicated 20 amp
circuit to feed that bathroom. And of course also
on that circuit you feed an exhaust fan too.
As I mentioned before, everything is 'relative' - it shouldn't be too difficult for a willing knowledgeable homeowner to run a few circuits. From an inspector's view, we see only the worst case scenarios - I'm sure there are guys who can be self-taught and do an adequate job.
Go ahead and dive right in there - it appears you have common sense, respect, and caution for 'live' 'hot' circumstances
Your Sub-Panel (if installed properly), should have been fed by a 4 conductor service cable known as SER cable. In it's jacket should contain, 2 black conductors, one white conductor, and a braided aluminum ground. Correct?
How many spaces are in the sub panel? Hopefully enough for your studio (as I pointed out earlier)
More importantly: any branch circuits that are installed in that sub panel, should have all of it's grounds (sometimes bare copper), connected to the 'BONDED' side of the bus in the panel. The neutrals however should have all of it's (white jacketed wires), connected to the 'UNBONDED' neutral bus in the panel.
GROUNDING IS VERY IMPORTANT - Life Safety Issues, and if not properly done, can create line interference, 'HUM' etc..
And use 12/3 romex for insulated, separately grounded receptacles (as I mentioned above)
You can handle it
And as someone else pointed out, if your sub was already installed by a contractor, check the nomenclature (marking) on the jacket of the cable to see if the size wire matches the overcurrent device (main breaker), that feeds it from the main panel ..... and assuming that the FIRST panel was grounded properly, than that's all the grounding that you'll need for your sub-panel. For a 100 amp sub panel, the feeder installed should have been 4 conductor no. 2 SER cable. For a 60 amp. sub panel, the feeder installed should have been 4 conductor no. 4 SER cable.
The 100 amp. SER cable should have been protected by a 100 amp. double pole breaker in the main panel. The 60 amp. SER cable should have been protected by a 60 amp. double pole breaker in the main panel.
c7sus mentioned:
"I don't know if you can buy a single-phase sub-panel. I've never seen one."
4 conductor SER service cable is made specifically for 'SINGLE PHASE' Residential Sub Panels (read my explanation above)
Many times larger homes with add-on construction (additions, garages etc.), have single phase sub-panels installed
Keep me posted, and I can help - I have a large data base of diagrams etc.
Best Regards
Michael Fraticelli
ROCKON@ucwphilly.rr.com
Hello again - Velvet Elvis
Sorry if some of this stuff I state here is already familiar to you...
You mentioned:
"I'm not required to have a licensed electrical contractor... only that I pass the city's electrical code test"
This is very common in a lot of municipalities outside of Philly.
My Mom lived in North Jersey, and although I'm BOCA certified as an Electrical Inspector, I didn't need to hire a Licensed Electrical Contractor to install a new service for her house. However I needed to have it inspected by the township Electrical Inspector. He and I were members of the same organization.
As mentioned: 16a x 120v= 1920watts OR 1920 watts / 120 = 16 amps
Hair Dryers are considered to be on only for a short while,
so it wouldn't be necessary to install a dedicated circuit
or ONE single receptacle just for the hair dryer.
Although since 1996, the NEC DOES state that all
NEW bathrooms shall have a GFCI dedicated 20 amp
circuit to feed that bathroom. And of course also
on that circuit you feed an exhaust fan too.
As I mentioned before, everything is 'relative' - it shouldn't be too difficult for a willing knowledgeable homeowner to run a few circuits. From an inspector's view, we see only the worst case scenarios - I'm sure there are guys who can be self-taught and do an adequate job.
Go ahead and dive right in there - it appears you have common sense, respect, and caution for 'live' 'hot' circumstances
Your Sub-Panel (if installed properly), should have been fed by a 4 conductor service cable known as SER cable. In it's jacket should contain, 2 black conductors, one white conductor, and a braided aluminum ground. Correct?
How many spaces are in the sub panel? Hopefully enough for your studio (as I pointed out earlier)
More importantly: any branch circuits that are installed in that sub panel, should have all of it's grounds (sometimes bare copper), connected to the 'BONDED' side of the bus in the panel. The neutrals however should have all of it's (white jacketed wires), connected to the 'UNBONDED' neutral bus in the panel.
GROUNDING IS VERY IMPORTANT - Life Safety Issues, and if not properly done, can create line interference, 'HUM' etc..
And use 12/3 romex for insulated, separately grounded receptacles (as I mentioned above)
You can handle it
And as someone else pointed out, if your sub was already installed by a contractor, check the nomenclature (marking) on the jacket of the cable to see if the size wire matches the overcurrent device (main breaker), that feeds it from the main panel ..... and assuming that the FIRST panel was grounded properly, than that's all the grounding that you'll need for your sub-panel. For a 100 amp sub panel, the feeder installed should have been 4 conductor no. 2 SER cable. For a 60 amp. sub panel, the feeder installed should have been 4 conductor no. 4 SER cable.
The 100 amp. SER cable should have been protected by a 100 amp. double pole breaker in the main panel. The 60 amp. SER cable should have been protected by a 60 amp. double pole breaker in the main panel.
c7sus mentioned:
"I don't know if you can buy a single-phase sub-panel. I've never seen one."
4 conductor SER service cable is made specifically for 'SINGLE PHASE' Residential Sub Panels (read my explanation above)
Many times larger homes with add-on construction (additions, garages etc.), have single phase sub-panels installed
Keep me posted, and I can help - I have a large data base of diagrams etc.
Best Regards
Michael Fraticelli